How to interpret the voltage of the MS side of trafo in LS grid calculation. #88
Replies: 1 comment 1 reply
-
|
Hi @willemijnbrus , Your colleagues' approach of being conservative by restricting limits from 0.9-1.1 p.u. to 0.95 to 1.05 p.u. is a logical one. A better way can be to directly tackle this issue: Run a powerflow using (Tip: PGM now supports multi dimensional batch calculations (https://power-grid-model.readthedocs.io/en/stable/examples/Multi-dimensional%20batch%20calculation%20example.html). Making such batches is hence easier and efficient.)
|
Beta Was this translation helpful? Give feedback.
Uh oh!
There was an error while loading. Please reload this page.
-
Hi pgm,
We use the pgm on LS grids from connections untill the MS/LS transformer.
Because we dont have information about what happens above the 10KV side of the grid, i think in our loadflow we/pgm automaticall assumes the 10kv as a stable input. However, colleages pointed us to that in real life of course this is a dynamic unit and not a stable. They pointed to us if we cannot take the 10KV as a dynamic component in our loadflow, we should at least then monitor our voltage boundaries at connections at 218,5 and 241,5 V rather than 207 en 253 Volt.
-is my understanding from pgm correct that we have to assume the 10kv side of the trafo as a give as we don't have in scope data on higher parts of the grid
-is this feedback familiar to you in other projects that focus on LS grids and do you know if in other projects then the solution is to use the 218,5 and 241,5 V rather than 207 en 253 Volt?